Old 11-07-2008, 02:17 PM   #11
qbee42
Senior Member
 
qbee42's Avatar
 
Join Date: Mar 2006
Location: Northern Michigan
Posts: 10,477
My Car: 2006 Prius
Model:
Package: #7
Thanks: 95
Thanked 391 Times in 290 Posts
Friends: 10
Default Re: Ready to make a UPS, just need some clarification

Quote:
Originally Posted by pt95148 View Post
Thanks everybody for the generous help here.
I have one more question that I forgot to ask, grounding.

The manual on the inverter says to ground it to the chassis, I am assuming here it is the car chassis, is this sufficient?

I think I saw in one design, maybe Problemchild, where he made an external ground plug into to house circuit.
Normally the inverter is grounded to the car chassis AND to earth ground (through a ground wire to the house or other AC load). The neutral wire on house wiring is already grounded to earth ground. If you don't ground the inverter to earth ground, you run the risk of having the entire car at 110VAC, so that grabbing the door handle could be fatal. It would take a failure for the car to become electrically hot, but that is why we use protective grounds. They protect against this sort of failure.

Tom
qbee42 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-07-2008, 08:16 PM   #12
Norm611
Member
 
Join Date: Aug 2005
Location: Western New York
Posts: 44
My Car: 2008 Prius
Model:
Package: #5
Thanks: 0
Thanked 0 Times in 0 Posts
Friends: 0
Default Re: Ready to make a UPS, just need some clarification

Quote:
Originally Posted by qbee42 View Post
Norm, in this sort of situation voltage drop becomes a deal breaker long before overheating can come into play. You can't have overheating without voltage drop, and a nominal 12V system starts with such a low voltage that voltage losses quickly reach an unacceptable level. Otherwise your comments are correct, and safety would be the main issue.

Tom

Tom,

The voltage drop is a function of the resistance of the leads, which for a given wire size is proportional to length. With ~83A input current to the UPS when drawing 1KW, the voltage drop will be proportional to the length of the input leads. 12 ft (6 ft each for positive & negative) will have a total resistance of ~0.019 Ohms, causing a voltage drop of ~1.6V. If the battery is being charged @ 13.6V (HSD system on), the input voltage to the inverter will be 12V (its rated input voltage). That cannot be considered too much voltage drop.

The problem is that 83 amps flowing through 0.019 Ohms of resistance will dissipate about 130W, or nearly 10W per foot. This is over 16 times as much as the wire is rated for.

Note: if you were able to mount the inverter right next to the battery, with each #12 lead only about 1-1/2 ft long, the total resistance, and therefore voltage drop, would be the same as with the two 6 ft leads of #6 wire supplied with the inverter. The total power lost in the wire resistance would be the same, ~34W. With #6 wire, the power dissipated would be less than 3W/ft, with #12 wire, it would be nearly 11W/ft. #6 wire can safely dissipate 3W/ft, #12 cannot handle 11W/ft.

Norm
__________________
Mine: 2008 Silver Pine Mica - pkg 5
Hers: 2008 Driftwood Pearl - pkg 3
Norm611 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-07-2008, 10:56 PM   #13
ChapmanF
Senior Member
 
Join Date: Mar 2008
Location: Indiana, USA
Posts: 249
My Car: 2001 Prius
Model:
Package: Base
Thanks: 0
Thanked 0 Times in 0 Posts
Friends: 1
Default Re: Ready to make a UPS, just need some clarification

Quote:
Originally Posted by Norm611 View Post
#6 wire can safely dissipate 3W/ft, #12 cannot handle 11W/ft.
Hey Norm,

Where can I find the W/ft wire ratings you're using? I've always wanted to know that. I expect they'd depend on the insulation material, so I assume you're talking about the stuff that's sold as "primary wire" for automotive use? Do the tables also involve adjustments for ambient temperature or number of wires bundled together?
I know the N.E.C. does, for the sorts of wiring materials used in structures, but I've never really found an official source of the same info for auto wiring.

Thanks,
-Chap
ChapmanF is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-08-2008, 12:11 AM   #14
qbee42
Senior Member
 
qbee42's Avatar
 
Join Date: Mar 2006
Location: Northern Michigan
Posts: 10,477
My Car: 2006 Prius
Model:
Package: #7
Thanks: 95
Thanked 391 Times in 290 Posts
Friends: 10
Default Re: Ready to make a UPS, just need some clarification

Quote:
Originally Posted by Norm611 View Post
Tom,

The voltage drop is a function of the resistance of the leads, which for a given wire size is proportional to length. With ~83A input current to the UPS when drawing 1KW, the voltage drop will be proportional to the length of the input leads. 12 ft (6 ft each for positive & negative) will have a total resistance of ~0.019 Ohms, causing a voltage drop of ~1.6V. If the battery is being charged @ 13.6V (HSD system on), the input voltage to the inverter will be 12V (its rated input voltage). That cannot be considered too much voltage drop.

The problem is that 83 amps flowing through 0.019 Ohms of resistance will dissipate about 130W, or nearly 10W per foot. This is over 16 times as much as the wire is rated for.

Note: if you were able to mount the inverter right next to the battery, with each #12 lead only about 1-1/2 ft long, the total resistance, and therefore voltage drop, would be the same as with the two 6 ft leads of #6 wire supplied with the inverter. The total power lost in the wire resistance would be the same, ~34W. With #6 wire, the power dissipated would be less than 3W/ft, with #12 wire, it would be nearly 11W/ft. #6 wire can safely dissipate 3W/ft, #12 cannot handle 11W/ft.

Norm
Whoa there fella, back up the bus. I never suggested using smaller wire. This whole conversation is about extending the supplied wiring. Obviously you are going to burn the wires if you use under-rated wiring. Perhaps I assume too much (being an electrical engineer), but only an idiot is going to replace the supplied cable with something smaller.

As for your example, #6 wire is rated for 101A for chassis wiring, which is well over the 83A in your example. If you are going to bury it inside a wooden wall, then you may have problems.

It's perfectly acceptable to shorten the existing leads. It is also acceptable to lengthen the leads with the same or larger wire, but you need to watch the voltage drop. That was the point I was trying to make.

On my sailboat, I have a 1KW inverter installed with about 10 ft of cable (there and back). I used #00. I don't need that for safety, but it keeps the I^2*R losses down, which improves performance. The heavier wire also allows the system to function even after some degradation of the cable and connectors, which often happens in a marine environment.

As for the question about wire ratings, search for AWG wire. The AWG tables are available all over the Internet.

Tom
__________________
Black 2006 package #7
Northern Michigan
qbee42 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-09-2008, 03:28 PM   #15
ChapmanF
Senior Member
 
Join Date: Mar 2008
Location: Indiana, USA
Posts: 249
My Car: 2001 Prius
Model:
Package: Base
Thanks: 0
Thanked 0 Times in 0 Posts
Friends: 1
Default Re: Ready to make a UPS, just need some clarification

Quote:
Originally Posted by qbee42 View Post
As for the question about wire ratings, search for AWG wire. The AWG tables are available all over the Internet.
Hi Tom,

Have you tried that search? In Google the first three hits have AWG tables and give several different ampacity figures. One of them even explains why there's such a variety of ampacity tables:

The ability of a wire to carry a given amount of current is affected by a number of additional factors, which are not accounted for in the AWG table above. The ambient temperature of the surrounding air, wire insulation, and number of other wires bundled together [provided below].

Ampacity relates to the ability of the conductor to carry current [amps] before the cable over heats. I understand there are hundreds of Ampacity tables for many different conditions.
I was just wondering where Norm got the watts-per-foot dissipation figures he quoted, and what assumptions about insulation type, ambient, and environment they were based on. I haven't seen anything that quite so neatly rates wire for watts per foot before.

-Chap
ChapmanF is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-09-2008, 03:58 PM   #16
qbee42
Senior Member
 
qbee42's Avatar
 
Join Date: Mar 2006
Location: Northern Michigan
Posts: 10,477
My Car: 2006 Prius
Model:
Package: #7
Thanks: 95
Thanked 391 Times in 290 Posts
Friends: 10
Default Re: Ready to make a UPS, just need some clarification

Quote:
Originally Posted by ChapmanF View Post
<snip>
I was just wondering where Norm got the watts-per-foot dissipation figures he quoted, and what assumptions about insulation type, ambient, and environment they were based on. I haven't seen anything that quite so neatly rates wire for watts per foot before.

-Chap
The Watts per foot figure depends on the assumptions that you state, as well as the type of cable and how the cables are bundled. Capacity rating will fall into two broad groups: those from the manufacturer, and those set by regulation or industry standards. Ultimate failure will occur when the wire in the cable melts, or when the insulation melts or catches fire, whichever comes first. Safety standards and good practices are set well below the ultimate figures.

The best place to get dissipation figures is from the cable manufacturer.

Tom
qbee42 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-10-2008, 12:24 AM   #17
ChapmanF
Senior Member
 
Join Date: Mar 2008
Location: Indiana, USA
Posts: 249
My Car: 2001 Prius
Model:
Package: Base
Thanks: 0
Thanked 0 Times in 0 Posts
Friends: 1
Default Re: Ready to make a UPS, just need some clarification

Quote:
Originally Posted by qbee42 View Post
.... The best place to get dissipation figures is from the cable manufacturer.
Thanks, Tom, that makes sense. Probably only Norm will be in a position to reply with the sources and assumptions for the specific numbers he used.

-Chap
ChapmanF is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-11-2008, 10:16 PM   #18
Norm611
Member
 
Join Date: Aug 2005
Location: Western New York
Posts: 44
My Car: 2008 Prius
Model:
Package: #5
Thanks: 0
Thanked 0 Times in 0 Posts
Friends: 0
Default Re: Ready to make a UPS, just need some clarification

Quote:
Originally Posted by qbee42 View Post
Whoa there fella, back up the bus. I never suggested using smaller wire. This whole conversation is about extending the supplied wiring. Obviously you are going to burn the wires if you use under-rated wiring. Perhaps I assume too much (being an electrical engineer), but only an idiot is going to replace the supplied cable with something smaller.

As for your example, #6 wire is rated for 101A for chassis wiring, which is well over the 83A in your example. If you are going to bury it inside a wooden wall, then you may have problems.

It's perfectly acceptable to shorten the existing leads. It is also acceptable to lengthen the leads with the same or larger wire, but you need to watch the voltage drop. That was the point I was trying to make.

On my sailboat, I have a 1KW inverter installed with about 10 ft of cable (there and back). I used #00. I don't need that for safety, but it keeps the I^2*R losses down, which improves performance. The heavier wire also allows the system to function even after some degradation of the cable and connectors, which often happens in a marine environment.

As for the question about wire ratings, search for AWG wire. The AWG tables are available all over the Internet.

Tom
Tom,

I wasn't trying to imply that you were suggesting the use of smaller wire, in fact you stated the same or larger wire. If someone only half understood your post, and used a smaller, but shorter, wire while keeping the total resistance the same, there could be an overheating problem.

I was trying to point out that there are two limiting factors for the wire size to be used, 1) Voltage drop (IR losses) and 2) ampacity of the wire.

For 12 AWG wire, I assumed 20A capacity (the value allowed for household wiring). I know the capacity depends on many factors, and this value falls between the "chassis wiring" and "Power transmission" values given on the 'powerstream.com' website.

Chap,

Tom is right about where I got my figures. Power dissipated by a resistor (including a piece of wire) can be calculated by the formula I^2 * R. The resistance per foot is calculated from the table (which provides Ohms per 1000 ft).

My Watts per foot values were calculated from the current and the resistance-per-foot value from the table

Norm
Norm611 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-11-2008, 10:36 PM   #19
qbee42
Senior Member
 
qbee42's Avatar
 
Join Date: Mar 2006
Location: Northern Michigan
Posts: 10,477
My Car: 2006 Prius
Model:
Package: #7
Thanks: 95
Thanked 391 Times in 290 Posts
Friends: 10
Default Re: Ready to make a UPS, just need some clarification

Quote:
Originally Posted by Norm611 View Post
Tom,

I wasn't trying to imply that you were suggesting the use of smaller wire, in fact you stated the same or larger wire. If someone only half understood your post, and used a smaller, but shorter, wire while keeping the total resistance the same, there could be an overheating problem.

I was trying to point out that there are two limiting factors for the wire size to be used, 1) Voltage drop (IR losses) and 2) ampacity of the wire.

For 12 AWG wire, I assumed 20A capacity (the value allowed for household wiring). I know the capacity depends on many factors, and this value falls between the "chassis wiring" and "Power transmission" values given on the 'powerstream.com' website.

Chap,

Tom is right about where I got my figures. Power dissipated by a resistor (including a piece of wire) can be calculated by the formula I^2 * R. The resistance per foot is calculated from the table (which provides Ohms per 1000 ft).

My Watts per foot values were calculated from the current and the resistance-per-foot value from the table

Norm
Norm, thanks for the clarification. I sometimes simplify things to make them easier to understand, but that can leave room for misinterpretation. The engineer in me wants to spell it all out in detail, but then my posts start to read like a contract: "The heretofore said mentioned party of the first part..."

Tom
qbee42 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-12-2008, 12:23 AM   #20
ChapmanF
Senior Member
 
Join Date: Mar 2008
Location: Indiana, USA
Posts: 249
My Car: 2001 Prius
Model:
Package: Base
Thanks: 0
Thanked 0 Times in 0 Posts
Friends: 1
Default Re: Ready to make a UPS, just need some clarification

Quote:
Originally Posted by Norm611 View Post
... can be calculated by the formula I^2 * R. The resistance per foot is calculated from the table (which provides Ohms per 1000 ft).

My Watts per foot values were calculated from the current and the resistance-per-foot value from the table.
Hi Norm,

Thanks for responding - as for how you calculated the watts per foot that would be dissipated at a certain current, yes that's straightforward, I followed that.

My question was more about:

Quote:
Originally Posted by Norm611 View Post
... nearly 10W per foot. This is over 16 times as much as the wire is rated for.

...#6 wire can safely dissipate 3W/ft, #12 cannot handle 11W/ft.
That is, the source of your W/ft limits. Where did you find that #6 can safely dissipate 3 W/ft, #12 can't handle 11 W/ft, and the wire originally in question (was that #12 also?) can't handle 10/16 W/foot?

It sort of makes sense that there would be references giving wire dissipation limits in that form, but I don't know where to find them.

Thanks,
-Chap
ChapmanF is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Tags
clarification, make, ready, ups
Similar Threads
Thread Thread Starter Forum Replies Last Post
Clarification re: plug-in feature? Wander88 Gen III 2010 Prius Main Forum 19 08-28-2008 09:53 AM
need clarification for satellite radio Toddsuki Gen II Prius Audio and Electronics 12 06-13-2008 12:00 PM
Fuse Clarification AMARCUS Gen II Prius Technical Discussion 2 05-30-2006 12:39 AM
I saw this contained in one of the posts and need some clarification Amyshubby Gen II Prius Main Forum 15 05-04-2006 12:54 AM
Extended warranty clarification ctrapp Gen II Prius Care, Maintenance and Troubleshooting 4 09-25-2004 09:39 PM


Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -5. The time now is 02:45 AM.


Powered by vBulletin®
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 3.3.2