This is a discussion on Hurricane Ike - Floridian - YIKES! Prius as basic generator advice. within the Gen II Prius Technical Discussion forums, part of the Gen II (2004-2009) Toyota Prius Forums category; Possible real bad hurricane about ready to slam us here in Palm Beach County, Florida. I picked up a 750 ...


Hurricane Ike - Floridian - YIKES! Prius as basic generator advice.

Reply
 
LinkBack Thread Tools
Old 09-05-2008, 12:36 AM   #1
partipilo
Weirdo
 
Join Date: Sep 2007
Location: West Palm Beach FL
Posts: 76
My Car: 2008 Prius
Model:
Package: #2
Thanks: 0
Thanked 0 Times in 0 Posts
Friends: 0
Default Hurricane Ike - Floridian - YIKES! Prius as basic generator advice.

Possible real bad hurricane about ready to slam us here in Palm Beach County, Florida.

I picked up a 750 watt inverter, which I have a feeling that if I am irresponsible, and run it fully loaded, it might be able to blow that infamous 100 amp fuse. My big question is, in case that happens, how difficult is it to replace, and can it be done by somebody who has pretty basic automotive work experience? I'm a systems admin geek but on my old Jeep I have managed to change out the spark plugs, a fuel pump, radiator hoses, and an O2 sensor. Whatcha think?

I have a kill-a-watt thingy I got from ThinkGeek so that should help along the way, but in case it does blow, and its terribly expensive to fix, I will be more responsible with loading (ie plugging in a 13" tv instead of the 60")


And, if it is something user-replacable, it may be a good idea to procure a spare in case these hurricanes do slam into us. :-)

Last edited by partipilo; 09-05-2008 at 12:39 AM.
partipilo is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-05-2008, 09:19 AM   #2
Patrick Wong
DIY Enthusiast
 
Patrick Wong's Avatar
 
Join Date: Mar 2008
Location: Green Valley, AZ
Posts: 4,059
My Car: 2004 Prius
Model: N/A
Package: #9
Thanks: 21
Thanked 213 Times in 184 Posts
Friends: 44
Default Re: Hurricane Ike - Floridian - YIKES! Prius as basic generator advice.

One fuse is located under the 12V battery's red plastic positive terminal cover. When you remove the red plastic terminal cover, you should be able to see the small fuse block. That fuse is not particularly hard to replace.

The DC to DC converter fuse link is located within the main relay/fuse box near the inverter. If you remove the lid to that box, then you will see a rectangular plastic box with a clear plastic cover, around 5" long. This contains several fuse links and is not easy to replace.

If you plan to be irresponsible with your power usage, then it would be well to install an 80A fuse in the inverter power cable. Good luck with your survival planning.
__________________
2006 Highlander Hybrid 4WD-i
2004 Prius
2001 Prius (sold Feb. 2008, 75K miles)
2000 Ford Mustang GT conv.
Patrick Wong is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-05-2008, 10:59 AM   #3
lefat1
Fat Member
 
lefat1's Avatar
 
Join Date: Jul 2007
Location: Sunny S. Florida
Posts: 1,428
My Car: 2008 Prius
Model:
Package: #6 Touring
Thanks: 31
Thanked 35 Times in 19 Posts
Friends: 9
Default Re: Hurricane Ike - Floridian - YIKES! Prius as basic generator advice.

if you live in florida, why not buy a generator like i did. you can get them now pretty cheap. if not i know 1st hand some tool rental stores that will rent them for 30-40 bucks per day
lefat1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-05-2008, 02:01 PM   #4
bwilson4web
03 and 10 Prius
 
bwilson4web's Avatar
 
Join Date: Nov 2005
Location: Huntsville AL with 2003 Prius
Posts: 3,885
My Car: 2010 Prius
Model: III
Package: #1
Thanks: 148
Thanked 369 Times in 205 Posts
Friends: 20
Default Re: Hurricane Ike - Floridian - YIKES! Prius as basic generator advice.

Quote:
Originally Posted by partipilo View Post
. . .
I picked up a 750 watt inverter, which I have a feeling that if I am irresponsible, and run it fully loaded, it might be able to blow that infamous 100 amp fuse. My big question is, in case that happens, how difficult is it to replace, and can it be done by somebody who has pretty basic automotive work experience? . . .
Not a problem:

Prius - UPS Project

IMHO, you could go with a 1 kW inverter without a out problem and the ability to deal with a wider range of loads. You don't need the ferrite donuts, I had them so I used them. I don't think they do much good.

If you go by an RV place, you can get an 80-90A circuit breaker, if you want the additional protection on the 12 VDC circuit.

GOOD LUCK!
Bob Wilson
bwilson4web is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-05-2008, 02:22 PM   #5
KK6PD
_ . _ . / _ _ . _
 
KK6PD's Avatar
 
Join Date: Mar 2008
Location: Los Angeles
Posts: 1,159
My Car: 2008 Prius
Model:
Package: #5
Thanks: 88
Thanked 35 Times in 32 Posts
Friends: 11
Default Re: Hurricane Ike - Floridian - YIKES! Prius as basic generator advice.

Hello all, first off, any storm that has a Cat number assigned to it sucks!!

That being said some generator basics are needed.

You need to consider the maximum and rated power of the generator. This is important depending on what items you want to run off of your generator. Items such as toaster, lamps, and coffee makers are resistive, or constant loads and their total load can be calculated at amps x 1. Items such as saws and drills are reactive loads and while
the running load may be small, the starting load should be calculated at running amps x 3. Remember, after the initial start less power is required for actual operation.

Always remember that simple power management will allow a smaller generator to do a big job. Very seldom are all tools or appliances operating simultaneously. When calculating power requirements, consider the starting requirements are only for the initial start and then additional tools may be operated in addition.
Remember Ohm’s Law from High School Physics?
Watts = Volts x Amps
Amps = Watts/Volts

So if you have two of the numbers (e.g. volts, amps) then you can find
out the other (e.g. watts). This can help you to determine the rated
power that you’ll need from your generator.


MAXIMUM AND RATED POWER
The amount of power that a generator can produce is rated in watts (power).
For Example, a 2kw generator produces a MAXIMUM 2000 watts of power. This means the 2kw could provide power to 20 one hundred watt light bulbs at the same time. The generator would then be at its MAXIMUM power output

A generator should never be operated at its MAXIMUM power output for more than 30 minutes.

RATED power is a more reliable measure of generator power. It is the power that a generator can produce for long periods of time. Typically the RATED power is 90% of the MAXIMUM power.

LOADS
In the previous example, the light bulbs are the LOAD of the generator. The EM2500 generator can handle a LOAD of no more than 2000 watts maximum.

The light bulb example is called a RESISTIVE type load and the POWER it requires is pretty easy to understand. Other RESISTIVE types of LOAD are things like toasters, convection ovens, hot plates, curling irons, coffee makers, stereos and TV's. RESISTIVE LOADS are usually those that do not have electric motors.
Another load is the REACTIVE type and is a little more confusing. Typically, a REACTIVE load contains an electric motor. This type of load may require up to three times as much power (wattage) to START as it does to keep it running. Examples of REACTIVE type loads are air conditioners, refrigerators / freezers, furnace fans, well pumps, bench grinders and air compressors

RESISTIVE LOADS
The equation shows the relationship between watts, volts and amps in a PURELY RESISTIVE load. If you know any of the two variables, the third can be calculated.

Example: You want a generator to power a 1000 watt flood light. The light is 120V and requires 1000 watts of power. Using the equation, we can calculate that the floodlight will draw 8.3 amps of electrical current.
For REACTIVE loads, the equation shows only a general relationship between watts, volts and amps. That's because the power requirements for REACTIVE loads changes with operating conditions

REACTIVE LOADS
When determining the proper generator for REACTIVE type loads, you must consider three modes of operation:

Click the image to open in full size. STARTING - The electric motor requires more power to start. The starting power required can be THREE times the running amount.
Click the image to open in full size. RUNNING - The power required to run the electric motor after it has been started.
Click the image to open in full size. LOADED - When the electric motor begins to work (saw begins cutting wood), its power requirement will increase. This is not applicable for most household appliances.

LOAD POWER REQUIREMENTS
Here are a few ways to determine power requirements for various loads that are expected to be powered by a Honda generator.

Method 1, using estimating charts, can be used to get a general idea of the generator size.
Method 2, reading the motor data tag, is more accurate since the data tag information is provided by the motor manufacturer. Data tag information does not always show STARTING power requirements for REACTIVE type loads.

Hope this clears up some of the Generator confusion.

Remember, ...NEVER RUN AT MAX LOAD FOR MORE THAN 30 Minutes!!!

Good Luck, de Pat KK6PD

KK6PD is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-05-2008, 09:34 PM   #6
partipilo
Weirdo
 
Join Date: Sep 2007
Location: West Palm Beach FL
Posts: 76
My Car: 2008 Prius
Model:
Package: #2
Thanks: 0
Thanked 0 Times in 0 Posts
Friends: 0
Default Re: Hurricane Ike - Floridian - YIKES! Prius as basic generator advice.

Wow that was quite a long reply KK6PD!

Thanks everyone for the advice!

Regarding the generator thing, theyre noisy, and if no cane hits this year, and it sits a year till next season, or maybe 2 years, those cheap engines are notorious for being difficult to get running again. The Prius starting up its motor every little while to top up the battery is not much noise, and probably a ton more efficient then a little generator running continuously.

Last edited by partipilo; 09-05-2008 at 09:37 PM.
partipilo is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-05-2008, 10:57 PM   #7
Dave_PH
Senior Member
 
Join Date: May 2008
Location: Florida & DC
Posts: 2,416
My Car: Other Non-Hybrid
Model:
Package: N/A
Thanks: 31
Thanked 75 Times in 52 Posts
Friends: 1
Default Re: Hurricane Ike - Floridian - YIKES! Prius as basic generator advice.

Better to use yor car to drive to the other coast and take a few days vacation.
Dave_PH is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-06-2008, 04:57 AM   #8
partipilo
Weirdo
 
Join Date: Sep 2007
Location: West Palm Beach FL
Posts: 76
My Car: 2008 Prius
Model:
Package: #2
Thanks: 0
Thanked 0 Times in 0 Posts
Friends: 0
Default Re: Hurricane Ike - Floridian - YIKES! Prius as basic generator advice.

Quote:
Originally Posted by Dave_PH View Post
Better to use yor car to drive to the other coast and take a few days vacation.
ahh theyre not that bad. they just knock out power for a week and make everything a complete mess. few homes actually get bulldozed down i kinda look forward to a good 'cane, makes life interesting for awhile.
partipilo is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-06-2008, 04:13 PM   #9
KK6PD
_ . _ . / _ _ . _
 
KK6PD's Avatar
 
Join Date: Mar 2008
Location: Los Angeles
Posts: 1,159
My Car: 2008 Prius
Model:
Package: #5
Thanks: 88
Thanked 35 Times in 32 Posts
Friends: 11
Default Re: Hurricane Ike - Floridian - YIKES! Prius as basic generator advice.

Quote:
Originally Posted by partipilo View Post
Wow that was quite a long reply KK6PD!

Thanks everyone for the advice!

Regarding the generator thing, theyre noisy, and if no cane hits this year, and it sits a year till next season, or maybe 2 years, those cheap engines are notorious for being difficult to get running again. The Prius starting up its motor every little while to top up the battery is not much noise, and probably a ton more efficient then a little generator running continuously.

Just a couple of adds, I would recommend the "Honda" generator line, VERY QUIET!!! Also I converted to run on propane, burns cleaner, a BBQ tank lasts a day and a half, I keep 6 full ones in the garage. Propane will not degrade like Gasoline will and it will not gum up the engine. I have gone as long as a couple of years between starts, check the oil, turn on the propane hit the start button. Kaching, 6kW at my disposal!!!

And it easily hides in the garage!!! About 700 bucks or less depends where you shop!!

Good Luck de Pat KK6PD

Last edited by KK6PD; 09-06-2008 at 04:15 PM.
KK6PD is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-07-2008, 11:43 AM   #10
hobbit
Senior Member
 
hobbit's Avatar
 
Join Date: Mar 2005
Location: Bahstahn
Posts: 3,630
My Car:
Model:
Package:
Thanks: 0
Thanked 216 Times in 118 Posts
Friends: 0
Default Re: Hurricane Ike - Floridian - YIKES! Prius as basic generator advice.

Hey KK, are you talking about one of Honda's "inverter" series?
What did you do to convert to propane? [yes, all this is totally
prius-unrelated..]
.
_H*
hobbit is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Tags
floridia, hurricane, inverter, priups
Similar Threads
Thread Thread Starter Forum Replies Last Post
Prius as a Generator Revisited georgekessel Gen II Prius Modifications 40 12-18-2008 12:28 PM
Yikes – More Prius Damage! effwitt Gen II Prius Main Forum 13 07-30-2008 04:34 PM
Prius and hurricane evacuation Texguy Gen II Prius Main Forum 9 07-09-2008 07:27 PM
The Prius as an Emergency Generator? dave34733 Gen II Prius Main Forum 1 09-10-2007 11:39 PM
Prius Whole House Generator Cheap! Gen II Prius Technical Discussion 2 07-26-2007 06:20 PM


Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -5. The time now is 10:11 AM.


Powered by vBulletin®
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 3.3.2