EVSE and GFCI
Discussion in 'Gen 1 Prius Plug-in 2012-2015' started by Rebound, Apr 16, 2012.
  1. Rebound
    Rebound Senior Member
    3,964
    2,613
    Portland, OR
    I'm installing an outdoor outlet to use with my charger. My friend told me that the EVSE has its own GFCI (which I believe is true), and the current surge on plug-in was tripping his GFCI outlet, so he replaced it with non-GFCI. But since my outlet will be outdoors, that will be a code violation, unless perhaps I cut off the EVSE plug and hard-wire it to AC power inside a junction box.
    Any thoughts?
    49,402
    you're right about code. some gfci's are more sensitive than others. you might have to try another or a different brand. i havn't read about many tripping problems here.
  3. Tracksyde
    Tracksyde Member
    1,429
    761
    So Cal
    I had a sprinkler timer on its own circuit in the garage. I replaced it with a 2-recepticle GFCI outlet (Leviton branded one from Lowes) and I've had no issues with the GFCI while charging.
  4. drinnovation
    drinnovation EREV for EVER!
    2,027
    586
    65
    CO
    There are two types of GF plugs.. gfci and gfpe. The GFCI's designed for bathrooms/kitchens are rated for low amps (5 maybe 10 ma threshold) and very sensitive and those designed for outdoor use/garages are rated at 20 or 30mamps and much less sensitive. One is mostly protecting the house/equipment, the other a human life. You should check the code in your area to see if gfpe is allowed out outdoor sockets or the garage.
    If you hit a hardware store, make sure you are buying the right type.. both are often called gfci (and they can look identical though the gfpe will have a higher mamp trip current).
    2 people like this.
  5. bisco
    49,402
    i've never heard of a gfpe, but a 20A gfci was around $20. i think.
  6. SCDrJ
    SCDrJ New Member
    120
    Orange County, CA
    Somewhere else I remember reading that some 15A GFCI plugs will trip at lower trip currents. The PIP EVSE is drawing 12A from what I recall so you are close to the circuit limit in some cases.
  7. drinnovation
    2,027
    586
    65
    CO
    Its not the amps of the circuit that determine a gfpe, but the level of ground current detected.. You can have a 20A 5MA GFCI for your kitchen (often needed for big microwaves/freezers). In most localities the GFCI for a kitchen or bathroom must trip at 5milli-amps of residual current on the grounded side (i.e. short) and switch in a few miliseconds.
    a GFPE is also called a 30MA GFCI, a low-sensitivity GFCI, a garage or outdoor or equipment GFCI can handle up to 30mill-amps of current on the grounded side. Its much slower to "pop" and hence useful in garages and outdoors where water or other items can cause higher residual currents.
    Learn more about them here:
    Residual-current device - Wikipedia, the free encyclopedia
    2 people like this.
  8. bisco
    49,402
    i'll have to talk to the electrical inspector and see if they are allowed here.
  9. bisco
    49,402
    charged my pip twice today, no problem with the $3. home depot gfci.