Outlet and EVSE recommendations for a 30A max circuit?
Discussion in 'Prime Plug-in Charging' started by gene, May 19, 2021.
  1. gene
    gene Member
    98
    NH
    I live in a condo with a covered, but open air, garage in New England so condensation is a definite issue. There is a 208v 30A max (due to the wiring) electrical box that I have access to, can meter, and use for charging (HOA approved already).
    It sounds like adding a NEMA 14-30R outlet, and getting a 24amp EVSE with a compatible plug is my best best to future proof (to the extent I can with 30A).
    I was going to go with a ClipperCreek indoor/outdoor 24A NEMA 14-30... but they seem to be back ordered 4-6+ weeks, and I plan to pick up the Prime this weekend, and would like to be able to charge at home sooner.
    So, any other recommendations for a outdoor rated NEMA 14-30 24amp EVSE? Or other recommendations for different outlet/EVSE combos?
    (I'm aware of, but would rather not do a cable adapter for the Toyota EVSE, especially with the semi-outdoor application).
  2. jerrymildred
    jerrymildred Senior Member
    11,516
    14,120
    Tampa, FL
    Congrats!!
    Most EVSE are either 16A or 32A. 24A is harder to find, but I did spot this one on Amazon.
    It has a NEMA 14-50 plug and you'll need a 50A circuit to be legal with it since it's capable of pulling 40A even if you do have it set to 16A max which is all the Prime can take.
    I just use a $190 Duosaida with my 14-30R receptacle.
  3. Old Bear
    Old Bear Senior Member
    712
    1,049
    Boston, Massachusetts USA
    I'm not sure there is any problem with installing a 40A EVSE on a smaller circuit. The current available to the EVSE will be limited by the size of the circuit-breaker protecting it. The EVSE will "advertise" that it can make 40A available to any vehicle plugged into it, but would not be able to deliver that if the vehicle demanded more current than the circuit-breaker permits. This would be a problem on vehicles which want to draw as much current as the EVSE advertises.
    However, the Prius Prime will never ask for more than 16 amps, so there would not be a problem unless you get a vehicle with a bigger appetite.
    All that being said, you have a different issue with your 208-volt panel. 208-volts is typical of a three-phase supply and, while you can wire your EVSE across one phase of the three-phase circuit (and add a protective ground), I'm not sure how the Prime and the EVSE will respond to 208 volts versus the typical 220- to 240-volt service.
    I the best case, it will just slow the charging time by about 10% (2 hrs 30 min rather than 2 hrs 15 min), but it's also possible that your EVSE may interpret the 208-volts as a problem (like a brown-out) and disconnect, thinking it is a fault.
    Maybe someone more familiar with available EVSEs and using a single phase of a three-phase panel could speak to this.
    (I understand that some ChargePoint station in commercial settings deliver 208-volts because they are wired to one phase of a three-phase system. I also know that there are EVSEs made specifically for use with 3-phase circuits but these are expensive and designed for high-demand applications such as charging large commercial vehicles such as electric buses.)
  4. Elektroingenieur
    2,515
    3,260
    Three Touring
    If I were asked to evaluate such an installation (EVSE rated at 40 A connected to a 30 A branch circuit), I’d be inclined to reject it as noncompliant with the National Electrical Code (NFPA 70-2020). EVSE must be listed (625.5), and listed equipment must be “installed and used in accordance with any instructions included in the listing or labeling” (110.3(B)), including the branch circuit size and connection method. In addition, “Overcurrent protection for feeders and branch circuits supplying EVSE [ . . . ] shall be sized for continuous duty and shall have a rating of not less than 125 percent of the maximum load of the equipment” (625.41).
    At least in the photos I’ve seen, the label on Prius Prime cars says, “CHARGING CONNECTOR FOR ON-BOARD BATTERY CHARGER, 100V-240V 1ϕ 20A,” which would seem to include 208 V.
    EVSE suitable for use at 208 V would also be needed. The ClipperCreek LCS series (for example) can operate at 208 V, but as stated on pages 18–19 and 31 of the manual (PDF), this is allowed only when connected line-to-line in a Y-connected system, not from the high leg in a Δ-connected system.
    jerrymildred and Old Bear like this.
  5. Salamander_King
    Salamander_King Senior Member
    10,975
    8,870
    New England
    Before you forge ahead with the project, assess your situation and evaluate your need to have an L2 EVSE. Do you really need to complete the full charge in ~2hours? How often does that need arise? Generally speaking, if you are driving only once a day regularly, then overnight L1 EVSE charging covers almost all the charging needs.
    #5 Salamander_King, May 21, 2021
  6. jerrymildred
    11,516
    14,120
    Tampa, FL
    Thanks. I thought about looking it up, but it was pretty obvious to me that the "spirit of the code" is that wires have to be able to supply the maximum current the outlet (or hard wired device) can demand and the fuse has to be able to protect the wires.
    It would be easy for someone to plug in a car that demands more current and alter the max current of the EVSE to charge faster. That would trip the breaker, of course, but then anyone who doesn't know better can still change the breaker w/o upgrading the wiring.
    Elektroingenieur likes this.
  7. 3PriusMike
    2,977
    2,334
    Silicon Valley
    This is NOT correct. The EVSE has no way to know the size of your circuit breaker. The EVSE is relying on a proper installation with respect to the size of wires and the circuit breaker capacity. If whatever load you put on a circuit exceeds the breaker capacity based on the amount of overload and the time duration, it will just trip off. The circuit breakers have no communication capability...they just sense overheating.
    To be compliant with the electrical code a device can only require a continuous amperage of 80% of the rated capacity of the wires and the breaker.
    I am not an electrician, but this is all my best understanding.
    Mike
  8. JimboPalmer
    12,470
    6,866
    Greenwood MS USA
    To the best of my knowledge, 208v always means 3 phase. No single EVSE can use 3 phase. I do not think any Level 2 EVSE works on 208 volts. The best advise I can give you is "Get a local electrician and listen to them."
    208 Volts Is a Weird Voltage. Where Did It Come From? | Thermal Corporation
    Googling, both Volt and Leaf owners report that using one phase of a 208 v line is faster than 120 v and slower than 240v.
    #8 JimboPalmer, May 21, 2021
  9. jerrymildred
    11,516
    14,120
    Tampa, FL
    Most equipment that I've seen that runs on 240V says, "208/240."
    We had three phase 208 at our radio station in Honduras. Our mini split air conditioners all ran on that as did our two whole house package unit air conditioners and, of course, water heaters had no issue with it. The only problem was the most of the time, the 208 was more like 180-190. They did not like that at all, so we had line conditioners on all the air conditioners. We also had line conditioners on the refrigerators. Even our 120V gas drier needed a line conditioner because the voltage would go too low to open the gas valve.
    But that's a quality problem with the electric utility. Basically, if it runs on 240, it'll probably run on 208, just a little less efficiently.
    Old Bear likes this.
  10. Old Bear
    712
    1,049
    I think we're saying the same thing. Regardless of the rated size of the EVSE, the EVSE cannot deliver more than the rating of the circuit breaker. Even when connected to a 30 amp circuit, the electronics in the EVSE will tell the vehicle, "I am a 40-amp EVSE" but if the vehicle accepts that information and attempts to draw more than 30 amps, the circuit breaker will trip.
    As I wrote:
    And, as you correctly note:
    This this true, but if, for example, you install an outlet and you plug in a device, the outlet has no way of knowing what you're plugged in. So, say you plug in an EVSE capable of handling 40 amps but connect it to your Prius Prime which will not draw more than 16 amps, there's no issue.
    If you connect a vehicle which draws more current than the circuit-breaker rating, regardless of the rated size of the EVSE, the breaker will trip (as it should!)
    If your EVSE is hard-wired, both the code and good practice would require it be served by an appropriately sized circuit and circuit-breaker.
    Neicy likes this.
  11. gene
    gene Member
    98
    NH
    Thank you for bringing this to my attention! It looks like the Clipper Creek AmazingE can also hanle 208v with similar wiring. I think this is basically a setup where there are 2 hot wires rather than three, which (and I am not an electrician) looks like it is the only way to properly to wire NEMA 14-30R since it has 4 prongs (2 hot, nuetral, and ground)? I have no desire to put a NEMA14-50 on a 30amp circuit, especially in multi-family building--and will have the electrician handle this either way.
    From a bit more research, it also looks like some EVSE (e.g. the one that comes with the Nissan Leaf) definitely don't do well with 208v/16amp. While some others seem ok, the ClipperCreak seems like my best bet for Level 2 charging in this situation.
    Thanks all!
  12. 3PriusMike
    2,977
    2,334
    Silicon Valley
    Not exactly.
    If such a setup was inspected it would be considered out of code. Someone could buy your house and have an EV that draws more current than the Prime and the breaker would trip every time they tried to charge. Having the breaker trip is only a last resort safety measure, primarily intended to detect faulty equipment, faulty wiring as well as when someone plugs in too many devices.
    Mike
  13. jerrymildred
    11,516
    14,120
    Tampa, FL
    Well, maybe partly the same. You would need to install the right sized breaker and wires for the max current of anything that was hard wired, per the code that @Elektroingenieur kindly looked up and shared. But in the case of a receptacle, you would size the wires for the receptacle and the breaker to protect the wires. So, if the thing you wanted to plug into that receptacle was made to be able to draw more current than the rating of the receptacle, the plug would be different, making it impossible to plug it in to that receptacle.
    Good thinking. Yes, 208 and 240 are both two hot legs. 240 is both sides of a split phase supply while 208 is two legs off of a three phase supply with neutral. Each phase is 120 from neutral, but only 208 from each other. I don't think the EVSE is affected by 208 vs 240. Not having the 208-240 voltage on the label is probably just an oversight since 208 is so rare in residential power. The only thing the 208 might affect is the charger itself, which is in the car. Apparently they are also indifferent to the 208v240 question since the articles I've seen on home charging all refer to level 2 charging as 208-240. The only difference is that 208 won't be quite as fast as 240.
    Here's a helpful article for people just getting started. How to Choose the Right Home Charging Station? | ChargeHub
  14. gene
    gene Member
    98
    NH
    I also confirmed the JuiceBox chargers will work with 208v, and they can be set to limit max amperage (useful for the 30A circuit and also multiple chargers).
    While my local utility has no incentives, in some places you get get a $650+ JuiceBox for < $200, which for those that can take advantage of it, provides some nice future-proofing.
    jerrymildred likes this.
  15. jerrymildred
    11,516
    14,120
    Tampa, FL
    Good news!
    BTW, it should not be necessary to limit the max current of the JuiceBox unless you plan to plug in cars that will draw more than a Prius Prime.
  16. gene
    gene Member
    98
    NH
    If I do go with the JuiceBox, I will definitely configure it to limit to 24A in case we have friends over that want to charge, etc. I'm not too worried about tripping the breaker, but it seems pretty easy to configure, so might as well. Only reason I could see not to is if someone were to "borrow" use our EVSE without permission and then tripping the circuit couild be a feature.
  17. gene
    gene Member
    98
    NH
    As a followup, the charger was installed yesterday and is working great.
    Tis is in a three phase 208v Condo building where I have an electrical box at our parking space that is connected to the condo associations house panel, and the wiring supports 30amp max. We obviously needed to get Condo Board approval, and went with the following setup:
    • Added a 14-30R receptacle to the electrical box at our spot
    • Went with a JuiceBox EVSE (partially based on availability and rebates)
      • The JuiceBox will support setting the maximum amperage, which is currently set to 24amps (plenty for the Prime, a bit more for visitors)
      • Purchased a high quality 14-30P to 14-50R adapter to allow plugging the JuiceBox into the 14-30R outlet
    • To monitor electricity usage (part of the requirement from the Condo Assocaition to let us hook up to the house panel), we went with an Emporia Gen 2 Vue
      • There are actually 3 other spots wired similarly to ours, so we had all 4 hooked up to save anyone else the trouble (we have a neighbor that is likely getting an PHEV or BEV soon too)
      • I'm pretty impressed with the Emporia so far--it supports 3 phase/208, and super inexpensive compared to what the electrician was going to suggest
    Thanks again for all the suggestions/help here and hopefully this will help others in condos/shared parking sitautions in the future.
    jerrymildred and 3PriusMike like this.