What are the Economics of Super Insulating a Walk-in Freezer?
Discussion in 'Environmental Discussion' started by kenmce, Jul 20, 2022.
  1. kenmce
    kenmce High Voltage Member
    1,544
    515
    NY
    I'm installing a walk-in freezer. It comes with all of four inches (10 cm) of insulation, rated at R-25. This seems to be the current standard for all walk-ins available in the US. To my eye this seems ridiculously small for maintaining a 50 degree F (28 degree C ?) difference between inside and out. My HVAC guy thinks that going beyond this will get you diminishing returns, that you'll never save enough on electric to pay for it.
    I have a rough estimate that it costs $400/month to cool a 10'x12' (3.048 X 3.65 M ) freezer when electric is at .10/kilowatt hour. I could easily add foam insulation boards to the outside and double the thickness and R value, but don't know how much I would cut down on heat loss by doubling the insulation. Anybody know how to figure this?
  2. Leadfoot J. McCoalroller
    8,088
    7,568
    Pennsylvania
    2018 Prius c
    $400 a month with how much traffic?
    At a certain point, more insulation won't help because essentially all your losses are through the door whenever somebody goes in.
    ...I can't tell you if that point is R25 or a formula to verify, but that sounds low to me as well.
  3. kenmce
    1,544
    515
    NY
    Don't know, don't have it yet. None for half the day though.
    Agreed. I figure I'll get one of those heavy plastic strip curtains to help the door.
    I keep a smaller difference between the inside and outside of my house, and I insulated the walls and ceiling right up to the limits of what would physically fit.
  4. lech auto air conditionin
    830
    605
    261
    san francisco
    I agree with the above about adding the curtains on the door if it’s going to be high traffic it’s a good measure anyway
    50° walking here in San Francisco would not be bad are you keeping it in the house where it’s air-conditioned are you keeping it in a garage that is not conditioned and you live in a place where it hits 90 or 100° in your garage might get up to 110° ?
    temperature difference makes all the difference in the world
    There’s a heat load formula for every square foot of surface area to a known insulation value to a known Delta between the temperature of inside and outside you can calculate the BTU loss per hour.
    because they walk in freezer of that size kept in my garage here in San Francisco California or the average daytime temperature all winter long which is about six months is about 58°F.
    in the summertime her average temperature is about 68°F so you’re R28 value would probably be good here in San Francisco
    but if he went to Texas and kept it in a an non-air-conditioned garage hits 100° plus in the garage would even get hotter R28 would not do so well.
    If this has been purchased from a real freezer company With an educated sales person can follow the zone chart for your climate and then he would take that information follow his chart and they would already have the recommendations in a spreadsheet to make the correct sales to the correct climate zone. For software program since most everything is done by software now.
  5. Rmay635703
    Rmay635703 Senior Member
    2,669
    1,688
    Somewhere in Wisconsin
    2013 Chevy Volt
    A more important question
    can you use the heat the unit generates?
    and if not is it being effectively vented so you don’t need to air condition your heated freezer vent air?
    also the floor of the unit is likely the most critical to well insulate.
    Also if this freezer is located in a perpetually air conditioned building your “losses” to the freezer help cool your building. As long as the freezer you choose is more efficient than your central air cooling your building is only a positive, not a loss assuming of coarse you properly deal with the hot air making sure it doesn’t heat unwanted areas
  6. fuzzy1
    10,452
    That also seems absurdly small to me. For homes in cold climates with smaller average (not worst cold nights) temperature differences than that, R-25 is the minimum for walls, and way short for ceilings.
    That is 4,000 kWh/month, or 48,000 kWh/year, which is absurdly high for any normal home for all energy combined, let alone a single appliance. My all-electric home never exceeded 12,000 kWh/year when it used electric resistance heat, and is now down under 6,000 kWh/year thanks to various improvements and heat pumps. (And I generate all that with rooftop solar PV.)
    But the back-of-the-napkin calculation below suggests a much lower energy need, maybe he slipped a decimal place? Or am I missing something big?
    Doubling the effective R value will cut the energy loss in half, absent other loss mechanisms such as open doors. Beware that effective R value is less than the listed R value of the raw insulation, due to greater heat conduction from thermal bridging through studs and other structural elements. Though if you offset the extra outside foam panels from the inside panels, you can reduce that thermal bridging.
    With R-1 insulation, you'd have a heat flow of 1 BTU per hour per degree-F per square foot of insulated surface (including walls and ceiling, not just floor). For a room 10x12' feet wide and 8' feet, that means (excluding corner effects and thermal bridging and any convective losses from air infiltration) heat loss = 592 square feet * 50 degrees = 29,600 BTU/hour. A true R-25 insulation would drop that to 29,600 / 25 = 1184 BTU hr, or about 350 watts. Allowing for those thermal bridges, make that 700 watts thermal. Assuming a refrigeration plant coefficient of performance of 2 (not leading edge at all), maybe 350 watts electric, or 260 kWh/month, or $26/month at your energy rate. Which seems suspiciously small, because it is similar to old era kitchen refrigerators with far less volume and wall area.
    Absent some bone-headed errors or omissions in this calculation, I could imagine $40/month, but not $400/month.
  7. lech auto air conditionin
    830
    605
    261
    san francisco
    My True 3 door commercial kitchen 73 ft.² refrigerator with a lot of active use approaches $40 a month extra electricity after installing in the house.
    On a high use day it’s amazing how much heat could come off of one of these Commercial refrigerators and they’re a little noisy. Compared to our residential refrigerators.
  8. Rmay635703
    2,669
    1,688
    2013 Chevy Volt
    $40 of electrically powered Air to Air heat pump “heat” is enough to heat a small home in a mild climate.
    Traditional home Refrigerators are notoriously under insulated, focusing on useable interior area more than insulation (my 5 year old fridge has 1.5” wall width in many spots)
    more efficient models just use more efficient cooling systems .
    Although the net heat output of a fridge isn’t huge, (one part cools, the other heats, zeroing out some heat)
    if you can isolate the hot side and the cold side you do end up with a pretty good separate cooling and heating system.
    My relatively small fridge makes about 1000BTUs if you don’t subtract the cooling affect. (Which is also not insignificant)
    Unfortunate most normal home refrigerators don’t at least offer preinstalled attachment points to have air vent / intake. My fridge is on an outer wall by a window so ducting in the summer would be easy.
  9. bisco
    51,933
    i would love to duct the heat outside. 94 out, 76 in, only makes sense
  10. fuzzy1
    10,452
    In a temperate climate, divert-able ducting to choose to send the heat inside or outside would be a useful energy saver.
    In a hot or AC-dominated climate, make sure the heat is dumped outside, not in the living space.
    On a year-round basis, at OP's electric price, that could cover not just the heat pump heating, it could cover all the other electric needs of an entire all-electric household too. Though the house would need to be more energy efficient than average.
  11. kenmce
    1,544
    515
    NY
    This is not a household refrigerator. This is a commercial freezer with enough space inside it to hold dozens of household refrigerators. The original plan was to buy new and get a unit designed so you can vent the heat inside the building during the winter and outside during the summer. Since then inflation has gotten severe, there are oddities in the freezer market, and we have settled for a used unit that dumps waste heat outside at all times.
    It is going to have its own room. The room will be climate controlled and kept at 50 to 70 degrees F (C 10 - 20), the proper temperature for dry goods storage. So figure if it's zero degrees F in the freezer and fifty degrees F in the room, then those skinny little four inch walls are maintaining a fifty degree (F) difference between inside and out.
    I got cost of operating estimate from:
    Operating Costs for Walk-In Coolers & Walk-In Freezers I expect a manufacturer should know.
    My unit is the 10 x 12 one and the $400/month for electricity figure is rounded down from their estimate. I'm rounding all my figures, I don't have precise numbers and don't want to pretend.
    I was considering putting down 2" of foam board before putting down the floor that comes with it. I don't want to do more because I don't want to have a huge ramp to roll stuff up.
    I don't think heat loss halves every time thickness doubles. I believe you get the most savings with thinner insulation and that gains tapers down as you add more and more thickness.
    I have been looking over the panels of the new unit and there is terrible bridging along every panel edge. The center of each panel may be R 25, but the edges have all the R value of a naked two by four.
    in the summertime (here) average temperature is about 68°F so your R28 value would probably be good here in San Francisco
    I'm in NY. This week its in the 90s F (32 C) winters it can get down into the single digits. (-12 C)
    #11 kenmce, Jul 21, 2022
  12. lech auto air conditionin
    830
    605
    261
    san francisco
    Also forgot to mention San Francisco California or most everybody is paying over the base price of PG&E rate instead of $.24 which is almost impossible to use that small amount of electricity that they give you a allotment were usually paying $.34 a kilowatt hour to $.38 a kilowatt hour and if you use way too much electricity they super penalize you at $.42 a kilowatt hour
    and commercial kitchen refrigerators are not meant for efficiency
    they were designed to be used in the kitchen with a lot of workers that will be continuously opening and closing the doors and this has three large doors.
    they were designed for quick cool down because fresh dishes of food and products will be put into the refrigerators that needs to be cooled down rapidly and that takes a lot more energy.
    so this is one of the disadvantages of owning commercial restaurant appliances in a residential house.
  13. fuzzy1
    10,452
    That example burns energy like a commercial facility, vastly more than an entire normal upper-middle-class all-electric home should use. At the example's electric price, it adds $5000 / year to the electric bill. What is your electric price? Note that plenty of areas charge double or triple the rate of that example.
    In some areas with nosy utility employees or drug enforcement agents, you'd want to notify the utility just why your electric usage is taking such a huge jump. Otherwise, it just might be used as probable cause to get a search warrant to come inspect for an illegal marijuana grow house.
    It would, if wall insulation is the only heat loss path. But that is normally not the only path. When a lot of heat flows through open doors or air leaks, all bets are off. Note also that when people double the wall insulation, they may not similarly double the door and door seal insulation, where a lot of thermal bridging occurs.
    That is the nature of the reciprocal math. Compared to 1" insulation, a 2nd inch saves 50%. The next 2 inches saves 25%. The next 4 inches saves 12.5%. The next 8 inches saves 6.25%. The next 16 inches saves 3.25%. ... The return per dollar or inch of added insulation diminishes rapidly.
    But the typical electric bill in the link above is totally out of whack for R-25 insulation. Either the cooler is leaking like a sieve, or the refrigeration plant is horribly inefficient, or the blower fan inside is seriously overpowered, or the room is being used to freeze a very large new mass of water or product every day. Or some combination of all of these.
    A sample computation for an 8' x 10' x 12' box with R-1 insulation, a refrigeration plant with a coefficient of performance of 2.0, and the door always closed, gives a lower electric bill than shown in that link.
    The example link is a decade old. I'd look to see if they have improved their thermal efficiency since then.
    #13 fuzzy1, Jul 22, 2022
  14. rjparker
    rjparker Tu Humilde Sirviente
    10,151
    6,309
    Texas Hill Country
    Once you are at r25 on a commercial 10 x 12 ft walkin freezer kept around 20f, air sealing is the best bang for the buck. So the door gasket, closing mechanism and refrigeration line penetrations are key. Most losses are staff keeping the door open as they access the space.
  15. lech auto air conditionin
    830
    605
    261
    san francisco
    Yes correct the statement that doubling your insulation does not cut your losses in half.
    it’s not a linear gain in insulation value.
    on refrigerators and especially freezers in low temperature application the most crucial thing is the skill set of the installers simply throwing up the walls floors and ceiling is not good enough.
    it’s how thoroughly they throw the caulking strips or whatever timer ceiling material they’re going to use in between the wall panels as there but it up next to each other.
    The floor must be completely sealed every ceiling panel all those gaps in between.
    One of the projects I’m working on right now I’m working on refrigerated rooms that we’ve installed that are 40 foot long 27 foot wide and 16 feet tall.
    I noticed their contractor they hired to actually do the installation got the cheapest work he can for workers and it shows.
    I told the owner that they were not doing it correctly.
    and when all is said and done they were having a problem with the humid air being sucked in through the cracks in condensating in the difference in temperatures of the metal wall turning into water and pouring out the bottom of the inside of the walls this is a very common thing that over the years cause Foister damage more than mildew and the interior side of the metal walls to rot out.
    where they set the ceiling panels on top of the walls was not flush and straight and they did a very poor job of putting in the foam insulation and I was able to prove this with my infrared camera showing all the cold spots and can see where all the air is infiltrating through the cracks and turning into liquid water on the inside of the panels and then dripping out at the bottom of the floor.
    how airtight and sealed it is is extremely important.
    and if you were to turn it into a freezer for example for ice cream -10 below zero to -20 below zero the problem becomes even 10 times more important to be airtight.
    our walls are 9 inches thick and the ceilings are 12 inches thick.
    fuzzy1 likes this.
  16. rjparker
    10,151
    6,309
    Texas Hill Country
    Lech has a decent youtube channel for those who did not know. One of my favorite hvac channels is in the same general area of northern calif, eg NorCal Refrigeration. A mild mannered university industrial ac and refrigeration specialist by day, NorCal Dave turns into a commercial hvac SuperTech after hours and weekends with his custom university surplus Vangina.
    For those who think a walk in cooler can be ordered from Lowes, here is the basic construction of this class of commercial cooler. This one is not a freezer but you get the idea.
    #16 rjparker, Jul 22, 2022
  17. kenmce
    1,544
    515
    NY
    You're paying 3x to 4x what I pay. How long of an extension cord have you got? I might be able to get a time-of-day meter. Right now its all lumped together. If I were penalized for using more power I'd probably get it its own meter.
    I assumed they were optimized for ease of assembly and low initial cost. Since my interests are different, that's why I'm looking at super insulation.
    I will have this when we take a delivery of frozen food. We don't get deliveries every day.
    It's in a restaurant type facility, not my kitchen.
    It is a commercial facility.
    ten or eleven cents per kilowatt hour, but I suspect it is going to go up. How much I cannot say.
    No, nobody gets to asset forfeiture my beautiful new walk-in!
    If humanly possible, I plan to be there when it is assembled. I don't want to be some numbskull sidewalk superintendent, but I do want a good seal on all those joints.
    How would one go about improving the doorway, without making it hard for people to use? Would it be useful to have a heavy quilted curtain that draws over the outside of the door nights and weekends?
    This is the crux of the matter. If doubling the insulation costs me, let's say $ 2,000 extra, and I save all of fifty cents a month on the electricity, then it would be a foolish project. If I can save fifty dollars a month on power, now it looks smart. Other people must have gone through this decision before me, and I'm hoping someone here knows how to work the math.
    If you take a look at: How Much Does It Cost to Run a Walk-in Cooler or Freezer? These people are an HVAC shop in Eugene, OR and their estimate for a 10' by 10' freezer (A little smaller than mine) is $350/month, not that far off from the estimate in the first post.
    I cannot dispute your math, however I must also respect their professional experience.
    All the more reason for me to be present for the install. Any comments on the best or worst ways to seal around the lines?
    I have hired on a local HVAC contractor who we have worked with for years. Men who get hired on there tend to stay there for a long time.
    I think it would have to be silicone. The panels pull up tight to one another. On the two sides that face the walls there will be no way to go around the outside using metal HVAC tape on the seams.
    I was talking with one of their men about ice build up and he said if warm air leaks in through a crack you'll always get ice. If I want ice I can put it there myself.
    We had something like that with a hotel that went up recently. We have plenty of good carpenters and sheet rockers right here, but every morning at 5:00 AM a little bus with New Jersey plates would show up, men would jump out, they would work a long damn day, jump back on the bus, and be gone. No one local seems to have spoken to any of them. I spoke with the locksmiths who came behind them and installed doors and locks for the facility, and they said there was not one straight or level wall on the entire property, and every door opening was just a little off from the last.
    What management saved by hiring these mystery men they lost when other people had to work with the results.
    I have notice that FLIR equipment is coming down in price. Do you have any opinion about those heat sensor units that you plug them into a cell phone?
    Not jealous. Not getting jealous. No, not at all jealous. (Shakes tiny fist.)
  18. Rmay635703
    2,669
    1,688
    2013 Chevy Volt
    If your not on a slab is there an opportunity to insulate externally in the floor joists below?
  19. kenmce
    1,544
    515
    NY
    The floor is a concrete slab. It does have 2" (50 mm) of foam under it for an R of 12 (RSI 1.5) I was thinking to put more under the floor of the freezer itself, since they will be kept at different temperature.
  20. fuzzy1
    10,452
    I believe a typical commercial facility has a lot of regular foot traffic going in and out, and a lot of product moving in and out. That means the bulk of the energy is blowing and flowing and being carried through the door when it is open, not through properly built walls.
    Being in a commercial facility, its power consumption shouldn't arouse the same suspicions as a normal home. Even if it did, being a fixed asset, it would pass muster if they don't find a huge array for grow lights inside.
    I think this would be a large factor in getting it done well.
    Go back to the math I posted earlier. If the walls are properly built and sealed, the calculation should be in the ballpark for that portion of the energy load, even if it doesn't account for a far greater load due to door traffic and needing to re-chill new product brought inside.
    If you add 2" extra to the original 4", that should drop the wall leakage load by 1/3rd. Where I figured $26/month, your added 2" would save about $9/month. Since R-25 insulation in a wall doesn't really make an R-25 wall due to thermal bridging from structural elements, offsetting seams to reduce those thermal bridges could get you 1/3rd of a somewhat larger number, but your savings would probably still be under $15/month.
    In short, to get the electric bills in the sample calculators, the bulk of the energy loss is not through properly built walls. It is through the door, especially when open, and through leaks and other possible construction defects. Be on watch to minimize those.