Charging trips GFCI breaker

Discussion in 'Prime Plug-in Charging' started by vbmania3, Apr 27, 2023.

  1. vbmania3

    vbmania3 Junior Member

    Joined:
    Jan 21, 2006
    7
    0
    0
    Location:
    USA - CT
    Vehicle:
    2022 Prius Prime
    Model:
    Limited
    I had a new Juicebox 32 installed in February with a 240 volt 50 Amp GFCI breaker to charge a 2022 Prius Prime. Often times when I start charging the breaker will trip within 30 seconds of plugging in. I have to reset the breaker (sometimes multiple times) and the charging will start and complete. The electrician says the initial surge of current causes the breaker to trip. The breaker support (Siemens) says they do not have other reports of this problem. What type of surge are we talking about to start charging? Anyone else have problems like this?

    DaveW
     
  2. Louis19

    Louis19 Active Member

    Joined:
    Feb 4, 2022
    347
    309
    0
    Location:
    Laval Québec Canada
    Vehicle:
    2022 Prius Prime
    Model:
    Upgrade
    I,m not an electrician but it seems to me it is not a huge surge, after all the load requested by car limits the current to 16 amp on 240 v.
    I have a 100 000 Btu pool heatpump protected by a 40 amps GFCI Breaker and the surge is far more superior than your case ,It is a Scroll compressor and it never trips...I don't think it's the car. For what I know GFCI mesures leakeage between Ground and Neutral
    Maybe @jerrymildred could chime in , if he is not on vacation
     
    #2 Louis19, Apr 27, 2023
    Last edited: Apr 27, 2023
  3. sam spade 2

    sam spade 2 Senior Member

    Joined:
    Mar 31, 2018
    7,035
    2,780
    0
    Location:
    USA
    Vehicle:
    2017 Prius c
    Model:
    Four
    FIRST you need to look closely at the breaker to see if it is tripping because of excessive current OR because of a perceived ground fault.

    I say "perceived" because a less than ideal connection anywhere in the circuit can cause the ground fault circuit to trip the breaker.
    Even a loose ground wire. And unless it is a 4 wire 240 circuit, there isn't even a passive "ground" wire present.

    Seems to me like it is a bit unusual to have a 240 circuit equipped with a GFCI.
    Is that required by code where you are ?
     
    Louis19 likes this.
  4. ChapmanF

    ChapmanF Senior Member

    Joined:
    Mar 30, 2008
    23,070
    14,974
    0
    Location:
    Indiana, USA
    Vehicle:
    2010 Prius
    Model:
    IV
    o_O a GFCI doesn't even need a ground wire. That's why code allows them to replace non-grounding receptacles on circuits that don't have a ground.

    The principle of the GFCI is really simple: the current-carrying conductors that pass through it (usually a black and a white, but all three if it's a two-pole breaker) must be carrying current that sums to zero. Everything going on one wire must be returning on the other (or on the other two).

    Any time the sum of the current on those conductors isn't zero, clearly some current is going someplace else, and the GFCI trips. Not a lot of chance to make the wrong call there.

    I do agree it's important to determine whether the breaker is tripping because of its overcurrent-protection function or its GFCI function.

    (For what it's worth, not long ago, I saw a drawing on the internet where somebody gave advice on connecting an exhaust fan to a GFCI, and showed splicing the fan's white wire directly to the white ones on the line side of the GFCI. The attentive reader may predict what that will do when the fan is turned on. :))

    Now, an AFCI breaker—for arc fault protection—does have a more complicated job. It has to recognize patterns of current draw that are typical of a flaky connection, but avoid tripping for things that can look a lot like that, say power tools or computer power supplies. I was recently reading about some AFCIs from Leviton that have upgradable firmware.

    Hard for me to imagine a GFCI ever needing upgradable firmware.

    But I wouldn't guess there's an AFCI involved in this thread. Unless the "GFCI breaker" that was put in was one of the newer dual-function ones.
     
    Isaac Zachary likes this.
  5. vbmania3

    vbmania3 Junior Member

    Joined:
    Jan 21, 2006
    7
    0
    0
    Location:
    USA - CT
    Vehicle:
    2022 Prius Prime
    Model:
    Limited
    The updated 2020 national code does require a GFCI for 240 volts in garages and outside areas now. May depend on the states implementation of this.
     
  6. ChapmanF

    ChapmanF Senior Member

    Joined:
    Mar 30, 2008
    23,070
    14,974
    0
    Location:
    Indiana, USA
    Vehicle:
    2010 Prius
    Model:
    IV
    Seemed like it used to be harder to find 2-pole GFCI breakers (I was looking around for one a few years ago to add to an old ConVerdant inverter. Now I notice them just hanging on pegs at Menards like regular stuff.

    Salty though.
     
  7. sam spade 2

    sam spade 2 Senior Member

    Joined:
    Mar 31, 2018
    7,035
    2,780
    0
    Location:
    USA
    Vehicle:
    2017 Prius c
    Model:
    Four
    BUT.....if there is a ground wire present, it needs to have a good connection.
    I know this from hard experience.

    But then.......with a 3 wire, 240 circuit, is there even a true GFCI breaker available ?
    I seriously doubt it.

    And if that does exist, in what circumstances is it used ??
     
  8. Louis19

    Louis19 Active Member

    Joined:
    Feb 4, 2022
    347
    309
    0
    Location:
    Laval Québec Canada
    Vehicle:
    2022 Prius Prime
    Model:
    Upgrade
    Well all I know is that a 2 pole 240vac GFCI breaker is monitoring imbalance between the 2 poles.If this happens some current is flowing to ground on the load circuit and the breaker trips.
    Electric code in my province , rules that 240 VAc electric outdoor apparatus operating closer than 10 feet from a pool or a hottub or spa must have a 240 Vac GFCI breaker installed
     
    #8 Louis19, Apr 28, 2023
    Last edited: Apr 28, 2023
  9. ChapmanF

    ChapmanF Senior Member

    Joined:
    Mar 30, 2008
    23,070
    14,974
    0
    Location:
    Indiana, USA
    Vehicle:
    2010 Prius
    Model:
    IV
    Yes; these days they hang on the pegs at Menards right there with other circuit breakers 'n stuff. Easy to find. Bit pricey though. You can see these are 3 wire, by the white pigtail that has to go to the neutral bus. The circuit neutral, of course, has to attach to the breaker.

    2-pole GFCI - Google Search

    In the familiar single-pole GFCI, the black and white wires simply pass through a coil inside the unit. As long as what's going on one exactly equals what's coming back on the other, the total current through the coil is zero and nothing happens. Let the current going and coming be slightly unequal for any reason (and there's only one possible reason: some of it is following some other path), and now there is nonzero current flowing through the coil, the coil shows an induced voltage, and the GFCI trips.

    To do it with a two-pole, three-wire circuit is no harder: just run all three, the white and both legs, through the coil. Normal operation will still have zero total current through the coil; it doesn't matter if what's connected is a 240-volt load and the current's coming back on the other leg, or a 120-volt load and the current's coming back on the white, or a combination with some of each. The total adding up all three currents will be zero, unless there is a fault current going someplace else.
     
    Louis19 likes this.
  10. vbmania3

    vbmania3 Junior Member

    Joined:
    Jan 21, 2006
    7
    0
    0
    Location:
    USA - CT
    Vehicle:
    2022 Prius Prime
    Model:
    Limited
    In talking to Siemens support for the CFCI breaker there are 3 conditions that can trip the breaker:

    The GFCI trip protections would be considered Overload, Instantaneous, and Ground Fault.

    Overload - thermal protection that when the breaker draws more current than the breaker is rated for a bi-metal element heats up. Once it has been heated up long enough (higher heat/current causes this to happen faster) the element will cause the breaker to trip.

    Instantaneous - a magnet inside of the breaker gets excited at the instantaneous pickup point and will cause the breaker to trip if an inrush current or short circuit causes the magnet to excite.

    Ground Fault - monitoring leakage current between the two hots (straight 240v circuit) or between the hots and neutral (240/120v circuit). If the imbalance exceeds the breaker's ground fault threshold (typically either 5ma or 30ma depending on breaker style) the breaker will trip.
    The instantaneous seemed to cause a problem with EV charging. The car basically tries to charge as quick as possible with a surge of current. This has been causes the breaker to trip within 30 seconds quite consistently in my case.

    The electrician has talked to many others that are seeing the same thing. Seems to be quite a problem for many electricians.

    I replaced the GFCI breaker with a normal breaker and have not seen the problem.