Home Solar

Discussion in 'Environmental Discussion' started by bwilson4web, Nov 24, 2024.

  1. tochatihu

    tochatihu Senior Member

    Joined:
    Apr 10, 2004
    10,008
    3,868
    0
    Location:
    Kunming Yunnan China
    Vehicle:
    2001 Prius
    Put effort into lightning protection for exposed items. There are nets and other forms of hail protection available. I guess they get deployed by climbing up there right before a storm turns nasty. Not everyone would want to do that.

    There are also specified resistant panels, and a handy hail-risk map

    What You Need To Know About Solar Power Hail Damage
     
  2. bwilson4web

    bwilson4web BMW i3 and Model 3

    Joined:
    Nov 25, 2005
    29,112
    16,554
    0
    Location:
    Huntsville AL
    Vehicle:
    2018 Tesla Model 3
    Model:
    Prime Plus
    This is what I have in mind:
    upload_2025-2-6_22-26-20.png
    • Two non-conducting posts or insulators along the apex of the roof
    • Pointy lightning rods, at each end of the ground cable
      • For esthetics, dull gray or black wire
      • How to keep birds from resting on wire?
    • Grounded away from the grid, service lines (on left) feeding the house
      • Pass through the bedroom attic to outside and down
      • Substantial ground rod to earth
    A lightning strike will still induce a substantial EMF in the regular house wiring. But TBD if surge protectors would work on Neutral, Hot_1 and Hot_2 to the earth ground. Fortunately the breaker panel is in the bedroom closet on the right

    Bob Wilson
     
  3. bwilson4web

    bwilson4web BMW i3 and Model 3

    Joined:
    Nov 25, 2005
    29,112
    16,554
    0
    Location:
    Huntsville AL
    Vehicle:
    2018 Tesla Model 3
    Model:
    Prime Plus
    Late thought, the cable to ground will be run inside:
    upload_2025-2-8_14-1-48.png

    A lightning strike will induce a significant magnetic field which is the start of a huge, EMI pulse. By running the ground wire through a ferrous conduit, to the extent capable, it should reduce the magnetic pulse. How much is question to test.

    Any retired electrical engineers out there?

    Found this research paper: https://www.osti.gov/servlets/purl/1875497

    Bob Wilson
     
    #63 bwilson4web, Feb 8, 2025
    Last edited: Feb 8, 2025
  4. tochatihu

    tochatihu Senior Member

    Joined:
    Apr 10, 2004
    10,008
    3,868
    0
    Location:
    Kunming Yunnan China
    Vehicle:
    2001 Prius
    Would you just get a young person up a ladder to remove those dead leaves? I tire of holding back commenting on that.

    The horizontal wire with be a bird perch no matter what. Why are you so intent on denying that? Oh you Canute you. But I can't see why you need it. The two grounded vertical pointy sticks will attract lightning better than metal frames of PV panels. Oh here's a thought - if PV frames have sharp edges, spend an hour or two on the ground softening the edges and corners. Like with a fingernail file. Very soft aluminiumiumium.
     
    Merkey likes this.
  5. bwilson4web

    bwilson4web BMW i3 and Model 3

    Joined:
    Nov 25, 2005
    29,112
    16,554
    0
    Location:
    Huntsville AL
    Vehicle:
    2018 Tesla Model 3
    Model:
    Prime Plus
    I have a question for @jdenenberg about running an insulated, heavy gauge ground cable/wire inside a ferrous conduit. Florida lightning research shows that as long as both conduit and cable are grounded at the same earth point, no problem.

    My first thought was the induced magnetic field would be somewhat attenuated by the ferrous, outer tube. This would reduce the magnetic field inducing an electric pulse in the house wiring. Then I thought, "rail gun."

    The high currents should generate a radial force that might make the ferrous tube into a lightning powered, pipe bomb. In effect converting a lightning fire hazard into something worse. But I may be over thinking the problem.

    The grid service line comes in on the Northwest wall of the house but runs in the crawl space to the circuit breaker panel at the opposite side of the house. Individual circuits are in the crawl space with the exception of the utility room on the North side extending into the back yard. If I run the lightning ground cable 90 degrees to the house wiring into the back yard, Northeast side of house, any induced EMF would significantly be weaker than if the grounding wire ran parallel:
    DJI_0074 copy.jpg
    • 200 A service line (red) comes from left to Northwest facing wall.
    • Service passed through crawl space to the circuit breaker (red box) panel in the Southeast bedroom.
    • All but one circuit pass through the crawl space.
      • Power to utility room, Northern most extension, passes through attic
      • Solar panel wiring in conduit in attic
      • 13 solar panels on Southwest facing roof
      • 3 solar panels on Southeast facing roof over porch
    • Lighning canary line about a meter above apex of tallest roof
      • Earth ground on Northeast back yard.
      • Tallest point, actual a lightning rod on the canary line at the earth ground.
    As for the birds, they would draw attention to the lightning canary line and leave guano behind. For rain collected, garden water not a problem. For other purposes, I'm not a fan of bird guano. There will be an owl puppet on one end and each panel array will have a rubber snake fixed to the bottom. The goal is to minimize nesting below the panels.

    Bob Wilson
     
  6. bwilson4web

    bwilson4web BMW i3 and Model 3

    Joined:
    Nov 25, 2005
    29,112
    16,554
    0
    Location:
    Huntsville AL
    Vehicle:
    2018 Tesla Model 3
    Model:
    Prime Plus
    Home solar panels have some maintenance:
    • cleaning
    • critter collections under the panels
    So I'm going to need to go up from time to time and I want to inspect some of shingles, about 4 years old. My home owner's insurance wants to know the 'damage resistance' which I had never heard of before.

    So this is how I've left the ladder for tomorrow:
    upload_2025-2-10_21-47-46.png
    Should there be a ladder problem, the roof of the BMW is a much shorter distance than to the ground.

    The ladder base is also held by a 2,800 lbs BMW bumper:
    upload_2025-2-10_21-47-22.png
    The major risk is transitioning from roof to ladder but I think it is covered.

    I will wait for my GF to help 'supervise' and call 911 if I screw up. But I'll be the one going to the roof since I'll also be inspecting shingles and later, the panels. Finally, installing the lightning protection and bird repellant owl and rubber snakes.

    Bob Wilson
     
  7. Trollbait

    Trollbait It's a D&D thing

    Joined:
    Feb 7, 2006
    23,749
    12,836
    0
    Location:
    eastern Pennsylvania
    Vehicle:
    Other Non-Hybrid
    Running the lightning ground through the attic seems like a bad idea, besides adding a potential leak point in the roof. There is an insane amount of energy in a lightning bolt. Forget EMF, and consider heat running along uninsulated wood. The bolt can also jump from the cable. More potential points it could jump to inside than running along the outside.

    Lightning rod installs just run along the roof and exterior walls. Looks like there is heavy gauge copper flashing for the grounding cable.
    Understanding The Basics - Residential Lightning Protection Systems | 4LP No need for a suspended wire. You do want another ground point coming off the far aerial instead of relying on all of a strike traveling across the roof.
     
  8. bisco

    bisco cookie crumbler

    Joined:
    May 11, 2005
    115,533
    52,927
    0
    Location:
    boston
    Vehicle:
    2012 Prius Plug-in
    Model:
    Plug-in Base
    Be careful, a ladder caused rotator cuff surgery, and i was fortunate at that
     
  9. bwilson4web

    bwilson4web BMW i3 and Model 3

    Joined:
    Nov 25, 2005
    29,112
    16,554
    0
    Location:
    Huntsville AL
    Vehicle:
    2018 Tesla Model 3
    Model:
    Prime Plus
    My current thinking is running the grounding wire under the exterior, eve of the roof. I want it to keep as dry as possible.

    Bob Wilson
     
  10. Hayslayer

    Hayslayer Active Member

    Joined:
    Nov 6, 2024
    540
    331
    0
    Location:
    USA
    Vehicle:
    2009 Prius
    Model:
    Touring
    You really should get the correct stand-off arms for the ladder. They attach near the top and will prevent the ladder from crushing the shingles at the edge of the roof like your ladder is doing. Those shingles are likely going to crack at the bend and fall off in the future. The arms also provide a very steady perch and make it easier to get on and off.

    And remember 4 to 1 for height/distance from base. Too steep and you're much more likely to tip backwards or slide sideways. All that extra height you have on that ladder may make it even harder to get on and off. Slide that thing a foot or so to the right and you have a pretty good step off!
     
    #70 Hayslayer, Feb 11, 2025
    Last edited: Feb 11, 2025
    Trollbait and bwilson4web like this.
  11. ChapmanF

    ChapmanF Senior Member

    Joined:
    Mar 30, 2008
    28,762
    19,087
    0
    Location:
    Indiana, USA
    Vehicle:
    2010 Prius
    Model:
    IV
    As far as I can tell, that paper is looking at effects where lightning current is sharing normal building electrical wiring, and wires are insulated and sharing a conduit.

    Your situation is much closer to that in the NEC section on "Enclosures for Grounding Electrode Conductors" (which see). I believe there's a similar provision (maybe even more emphatic) in the codes that are specific to lightning-system conductors, but I'm less familiar with those.

    The gist of the NEC provision is that the electrode conductor is allowed to run in a ferrous enclosure only if the ferrous enclosure itself is made an electrically parallel current path. It must either be an electrically continuous enclosure all the way from where the electrode conductor starts to the grounding electrode it leads to (and connected to both), or, if not, then every segment of ferrous enclosure that the conductor passes through must be bonded to the conductor itself at both the entry and the exit end.

    That may defeat, or partly defeat, your purpose to minimize the magnetic field seen outside, as instead of having the ferrous material enclose something carrying a current, it ends up carrying a big share of the current itself.

    So why do the NEC folks insist on this?

    Inductance.

    A lightning current has a crazy fast rise time, so even tiny inductances in the ground path matter. Every place your electrode makes even a ¼ turn around a corner, well, that's another ¼ turn, adding to the inductance. Count those and minimize. Could a different routing need an even smaller fraction of a turn? The larger the inductance, the more huge the voltage spike seen at the upstream end for such large dI/dt. It can be huge enough for some lightning to give up on your conductor and follow something else.

    A ferrous enclosure around the conductor—when it isn't bonded and sharing the current—is effectively running the conductor through an inductive choke. That's why the NEC guys say nay.

    https://www.ecmag.com/magazine/articles/article-detail/codes-standards-minimizing-choke-effect-understanding-ferrous-metal-raceway-bonding
     
  12. bwilson4web

    bwilson4web BMW i3 and Model 3

    Joined:
    Nov 25, 2005
    29,112
    16,554
    0
    Location:
    Huntsville AL
    Vehicle:
    2018 Tesla Model 3
    Model:
    Prime Plus
    I appreciate your insights. So our understanding:
    upload_2025-2-11_19-46-41.png
    • We agree the base of the conduit must be grounded to earth along with the conductor.
    I had not considered that a ferrous conduit would in effect make it an inductor that might induce a voltage gradient between the top and bottom, enough to arc over at the top and make it a parallel conductor. My concern was the would the induced magnetic field be strong enough to physically displace by expansion the conductor (i.e., the rail gun effect.)

    From the paper originally cited:

    upload_2025-2-11_19-58-56.png

    This leads me to believe any inductive effects on the lightning ground current are weak. But there can be capacitive coupling if not grounded at one end. But this was not my concern.

    So I read up on rail guns in Wiki and realized the ferrous conduit lacks a parallel, return current to make it act like an armature. This suggests a thought experiment. Form a "U" section in the ground wire with strong mechanical bracing and have an armature at the base of the "U" attached to a sign that reads, "Lightning was here."

    Bob Wilson
     
  13. bwilson4web

    bwilson4web BMW i3 and Model 3

    Joined:
    Nov 25, 2005
    29,112
    16,554
    0
    Location:
    Huntsville AL
    Vehicle:
    2018 Tesla Model 3
    Model:
    Prime Plus
    Thank you! Scampering up and down ladders is not one of skills. I especially like the "standoffs" and will get them.

    With a solar roof, I will have to periodically 'inspect' so these are valuable tips.

    Bob Wilson
     
  14. ChapmanF

    ChapmanF Senior Member

    Joined:
    Mar 30, 2008
    28,762
    19,087
    0
    Location:
    Indiana, USA
    Vehicle:
    2010 Prius
    Model:
    IV
    Still, the National Electrical Code 250.64(E)(1) explicitly forbids a configuration like the above, bonding the conduit at one end only. It is allowed to be bonded at both ends, or it is allowed to be of nonferrous material. Your choice.

    I believe the NEC editors have reached a different conclusion about the significance of inductive effects. The paper you have found may not be all that they have looked at. They may have interpreted it another way.

    Besides the NEC, the standards specifically for lightning protection installations are directly on point for your project.

    What Are the Basic Differences Between UL 96A, NFPA 780 and LPI 175? | nVent

    Where the NEC is about the building's ordinary wiring, and 250.64(E)(1) puts a requirement on the grounding electrode conductor because it can carry lightning currents, NFPA 780 is what will set out requirements specifically for a grounding conductor meant for lightning.

    It's too many years since I looked and I can't give chapter and verse at the moment, but unless I'm badly misremembering, that standard harps even more than the NEC does about minimizing the high-frequency impedance of the grounding path.
     
    #74 ChapmanF, Feb 11, 2025
    Last edited: Feb 11, 2025
  15. Trollbait

    Trollbait It's a D&D thing

    Joined:
    Feb 7, 2006
    23,749
    12,836
    0
    Location:
    eastern Pennsylvania
    Vehicle:
    Other Non-Hybrid
    The cables for lightning rods are just bare copper or aluminum, and just sit out in the elements. AWG 2 is the thinnest when using copper.

    Seems you can run them through the building interior.
    Lightning Protection Overview - Lightning Protection Institute.

    Work has multiple copper lines running down the building walls. My house still has its original wrought iron rod and conductor. The angle of the conductor is too tight going over the roof edge to under the eaves. A strike will likely jump off it, and hit the neighbors' place.
     
  16. bwilson4web

    bwilson4web BMW i3 and Model 3

    Joined:
    Nov 25, 2005
    29,112
    16,554
    0
    Location:
    Huntsville AL
    Vehicle:
    2018 Tesla Model 3
    Model:
    Prime Plus
    Ok, taking your advice:
    upload_2025-2-11_22-33-17.png

    So I started with:
    upload_2025-2-11_22-36-17.png

    I've scheduled my electrical service to visit on Friday to see if they will bid on installation of a lightning protection system. I also asked Mr. Google for local providers but no luck. So I find it mildly amusing that something Benjamin Franklin pioneered over 200 years ago seems so baffling.

    My original requirement dates back to repairing a TV directly connected to the cable service that was lost in a lightning strike. Taking down two trees, one 184 ft tall, means my house is more exposed to direct lightning strikes. Strikes that would find an expensive set of solar panels on the roof. After the electrician gets an opportunity to make a proposal, I'll reassess.

    Of course, it is possible that modern solar projects already take pains to deal with lightning risks. Something I will ask when the installation crew shows up.

    Bob Wilson
     
  17. bwilson4web

    bwilson4web BMW i3 and Model 3

    Joined:
    Nov 25, 2005
    29,112
    16,554
    0
    Location:
    Huntsville AL
    Vehicle:
    2018 Tesla Model 3
    Model:
    Prime Plus
    Everything including teams, arrived early:
    installation.jpg
    Shame about the rain but they came prepared.

    I called the local news offices to give them a "heads up."

    Bob Wilson
     
  18. tochatihu

    tochatihu Senior Member

    Joined:
    Apr 10, 2004
    10,008
    3,868
    0
    Location:
    Kunming Yunnan China
    Vehicle:
    2001 Prius
    I would not be at all surprised if a Huntsville Public Library has a print copy of UL 96a and a photocopy machine.

    ==
    electrochemistry.png

    looks like a bronze clamp and an anodized steel bolt. McMaster Carr calls them hex head screws:

    McMaster-Carr

    not that you need 10 or 25, but you may meet 9 or 24 friends online who don't want to get 'screwed' by electrochemistry either.

    ==
    You would buy the grounding rod locally? Install it in soil that seems likely to be wettest within 'reach' of your 60 feet of 6 awg. Use rebar to create its pilot hole because it's rocky down there.

    Make a 'flat' on the grounding rod where your clamp bolt will make its kiss.

    Opinions vary on whether to pour salt into the pilot hole before 'rod' makes his entry. A coin flip I guess.
     
    #78 tochatihu, Feb 12, 2025
    Last edited: Feb 12, 2025
  19. Trollbait

    Trollbait It's a D&D thing

    Joined:
    Feb 7, 2006
    23,749
    12,836
    0
    Location:
    eastern Pennsylvania
    Vehicle:
    Other Non-Hybrid
  20. ChapmanF

    ChapmanF Senior Member

    Joined:
    Mar 30, 2008
    28,762
    19,087
    0
    Location:
    Indiana, USA
    Vehicle:
    2010 Prius
    Model:
    IV
    Yeah, out of the three documents mentioned, I don't know that I would start (or even ever bother) with UL 96A. That'd be for if you want to hang out your shingle as a lightning system inspector. Don't get me started about UL. That's an outfit heavily geared to doing evaluations under $$$$ contract to deep-pocketed customers who need the service. Their document prices are out of this world, and they won't even approve an online account to browse their "solutions catalog" before you explain your employer and job title and how you're going to make them money.

    The ur-standard here is NFPA 780, from NFPA, the nonprofit that researches standards to help stuff not burn down. If you scroll down to the View Free Access button here and find the terms and conditions copacetic you can do that.

    NFPA 780 Standard Development

    Or you can buy it on trees for $157, or $141 if you're a NFPA member (which doesn't require you be anybody special, as long as you think it's nice for stuff not to burn down and willing to support a nonprofit $225 a year for that). Or you can take NFPA LINK ($12 a month or $115 a year for an individual) and view any of 1,500 of their codes and standards online going as far as five editions back.

    The LPI 175 standard is essentially a 78-page crib sheet based on NFPA 780:

    https://lightning.org/wp-content/uploads/2023/06/LPI-175-2023-REV.pdf

    I'm only about halfway through. :) The first 15 pages duplicate the overview web page Trollbait linked. The bond-your-metal-conduit-at-both ends provision (corresponding to 250.64(E)(1) in the NEC) is paragraph 33, found on page 23.

    My partially-formed opinion about halfway through this doc is that the amazon seller you found may not necessarily have read this. I would spend more time reading before installing and before the amazon return window closes.
     
    tochatihu likes this.